I am using a Red Lion G310 with a CompactLogix PLC and the "Allen-Bradley Native Tags via L5K File Enhanced" driver. I can import and use the tags just fine from the L5K file, but I am wondering if you can use the Allen Bradley hardware addressing also. I can't seem to figure it out.

For example, I can set an indicator to be controlled by [PLC1.ExampleTag], but it doesn't seem to work if I use [PLC1.Local:1:I.Data.0]. Is there some special syntax that I need to use, or is this just not possible?

Thanks for any help.
 
I don't think it is possible to address them directly. I always create Aliases for them.
 
Zlinger, I would recommend buffering the I/O tags regardless as the IO scan is asynchronous to the PLC scan. Specifically in your case, I believe the colon ":" in the tag name is what hangs up Crimson software.
 

Similar Topics

This is the set-up we have, and we recently lost comms to two devices on this PLC. After replacing the red lion and copying in another identical...
Replies
3
Views
1,861
Hi everyone! I'm trying to "bridge" some variables between a CompactLogix and an OPC UA-server using a Red Lion DA10D protocol converter. I got...
Replies
0
Views
1,350
Hi all, I'm designing a project using a CompactLogix L33ER PLC, connected via Ethernet to several PowerFlex 525 VFDs and a Red Lion HMI. As far as...
Replies
4
Views
3,913
Hey guys, I am trying to make an Allen Bradley Compactlogix and a Modicon Quantum talk to each other using a Red Lion Data Station. So far I've...
Replies
2
Views
3,012
I am having some fits with my new project. Here are the details of the system: PLC: 1769-L33ER v21.11 RsLogix Studio V21 HMI: G308C100 Crimson...
Replies
22
Views
9,460
Back
Top Bottom