Hi guys,

I have a system with several s7-1200 PLCs with identical program.

I want to connect the s7-1200 PLCs to one s7-1500 via profinet, which means, I need to configure the s7-1200 as I-device. the s7-1200 will be the IO-device and the s7-1500, the IO-Controller.

Now, what I want to know is, if do I need to generate individual GSD files for each s7-1200 or I can use one GSD file for all s7-1200?

Thanks and Regards.
 
You can use the same GSD file for all the S7-1200.

edit: WHen you add the GSD file for each S7-1200 to the S7-1500 you have to assign a unique device name, and it must match the one you actually assign to the actual S7-1200 PLCs.
 
Last edited:
I wouldn't do it that way
Just integrate 1200 and 1500 in the same project. Make the 1200 an I device with a check box. Then assign I and Q data. Done
 
Hi JRW,

Thanks for the reply. Actually, the S7-1200 is a different contractor so I cannot integrate it in my TIA project. We requested a GSD file from them. Now I want to make sure what are the configurations that I need to consider to be able to communicate with them.

@JesperMP: OK. I will check on the device name. Hopefully they assign a different device name for each 1200 PLCs.
 

Similar Topics

Hey guys, I have to take an upload of a program on an S71200 PLC to change a hardware config option and then redownload the program with this...
Replies
3
Views
111
I'm new to S7. Whenever I do a "Download to device", this window appears. I've seen some online tutorials and this doesn't happen for them, so my...
Replies
4
Views
1,080
I've just created a small program and saved it. Then I clicked on the 'Download to device' icon and this dialogue box appeared. Do I need to...
Replies
20
Views
1,425
Trying to integrate a new S7-1500 to an existing S7-300 PLC. Using the S7-1500 as an I/O Device. Trying to send some simple boolean tags between...
Replies
2
Views
1,080
Ciao guys, I'm not used to program on Siemens PLCs, but sometimes I have to. I'm experiencing a strange problem when I try to connect to a PLC...
Replies
9
Views
3,880
Back
Top Bottom