Good Morning ,
I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card.
Would you all a simple wiring diagram , of what terminals on the card , this RTD would wire to ?
Thanks so much , and have a great day .
You need a converter from PT100 to 0-2mA 4-20mA or whatever that input module accepts.
A good converter compensates for the resistance of the wires up to the sensor and linearizes the curve since the resistance-temperature relationship is not exactly linear.
The 1756-IF8 can be voltage or current input only. You need a signal conditioner to convert the RTD signal to a compatible input.
Many companies make signal conditioners.
Do a quick Google search for: " RTD Signal conditioners"
There are many different types of RTD to mA converters. 30.00 on up to a few hundred Dollars. Maybe if it's for room temperature, the 30 dollars works great. Does it matter if your off .2 of a degree? If it's etching something, .2 of a degree just ruined your product. What are you measuring?
George
Hi, I'm new here and very much a beginner. I had a question about this AB 1756-IF8 Analog card and how to correctly wire it. I looked in the...
4,051
Hello, Currently my IF8 is set as 1756-IF8/B Revision 2.011 and my PLC only register as 1.011 which I unable to get the data from the sensor...
1,494
Can you wire a 1756IF8 analog input card for passive and active instruments at the same time or do they have to be separated. Such as wire 1 card...
5,011
Hello! I am trying to wrap my head around how to wire a 4-20mA sensor to my AB 1756 ControlLogix IF8 Analog Input card. Could someone educate me...
3,869
Hello, I have a flow meter that has been in service for a few years now. I have recently noticed that my registration on the mag meter does not...
1,130