Hello,


I am commissioning a 1769-L33ERMS compact guard logix 5370 safety controller and am running into an issue with the safety ethernet devices.


I have 4 kinetix servos 2198-HXX-ERS2, an armorblock 1732ES and area scanner. I'm not very well-versed in cip safey and SNN and what-not. But what I am experiencing is that when the plc is in program mode, I can communicate with and read values from the safety devices, but as soon as I switch to run mode in the plc, the safety devices fault and timeout. A repeated faulted > connecting > running > faulted pattern.
The PLC does have time-synchronization enabled and is the master.


I'm at a loss for what to look for next, any thoughts?


Edit: Code 16#0203 - Connection timed out, error on the modules


Thank you!
 
Last edited:
Update: The safety task was executing at a rate too fast for the system to accommodate, lowering the safety task interval fixed the issue.
 

Similar Topics

Hi, I have an 1769-L33ERMS that I swapped out for a spare because it was causing issues. When power cycled it would hold the Ok and Safety Ok...
Replies
1
Views
605
Hi All, I have a safety compact logix PLC. I was wondering if anyone has experience in getting both of the ethernet ports on the device to have 2...
Replies
4
Views
3,329
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
98
I have a CompactLogix 1769-L31 and need to communicate with it. I only have studio 5000 on my computer. However, when I try to start a new project...
Replies
12
Views
398
I have a 1769-L24ER-BB1B and I am trying to flash it to 34xx, its flashing red and faulted, when I try to flash it I get a popup stating it needs...
Replies
14
Views
256
Back
Top Bottom