1769-L35E comm to Ethernet module MSG error
sparky mark
Jul 2008
Lititz, PA
using a 1769_L35E to communicate over Ethernet to an Ethernet module (non AB). Trying to attach a picture of the error message. Is there anything obvious that I am doing wrong? Can see the module from the PC (web page) it's like the PLC can not "see" the module over Ethernet. Have done this same application numerous times in the past. no problems.
Thanks in advance for any help.
Try checking the box for a "Connected" message, rather than unconnected. You'll likely have to do it offline and download.
I have found one device where I had to check this box or I got a strange, seemingly unrelated error - can't remember what it was, but it could have been the same one you're seeing.
What sort of device is this ? Does it have optional configurations to enable EtherNet/IP ?
If so, go download the TCPing utility from elifulkerson.com and ping it for TCP Port 44818, which is EtherNet/IP.
And for kicks, ping it for TCP port 502 (Modbus/TCP ) as well. I've seen quite a few devices that support both but get misconfigured.
That error code 16#3000 is unusual. Most ordinary TCP connection failures (due to timeout) show 16#0001 for the Error and 16#0203 or 16#0204 for the extended error.
Try adding , 1, 0 to your path (assuming your processor is at slot 0), maybe specifying to go across the backplane and Ethernet module slot might help.
sparky mark is not trying to communicate with an A-B controller
Hello, We have had a machine running for the last 10 years. It has 2 x Kinetix 300 drives. Around a year ago, one of the drives failed. We were...
429
Hi, I recently tried to change the IP address of my 1769-L35E Series A, since doing this the MS indicator is flashing red and the NS indicator is...
936
Good morning guys. Im triying to communicate 4 JXC91 with a 1769-L35E AB CPU. I already test the JXC91 with a newer AB CPU using eds files and...
1,460
Good Morning , I'm looking for a cheap 1769-L35E processor. I know this CPU is obsolete. I'm preparing for a obsolescence project , but the...
1,187
Hi Guys, Question - does the subject title AB processor act as a processor AND comms module? It does have communications ports available on the...
967