I have done about (3) 24VDC systems and have a late question...
I have been grounding the DC negative and have not seen any issues.

I am supplying 24VDC to PLC Power, PLC analog an ddigital IO, and Instrumentation.
I use 2 24VDC power supplies, 1 PS for all the Instrumentation and Analog IO and the other PS for Digital IO.

Gounding?
 
Just be sure to tie all the negative power supplies to one common bus. Don't daisy chain the negative terminals, of each of the power supplies. Then run one ground to a good solid ground, from the common negative bus, and not the 120/240 VAC mains ground.

-Chris
 
^ Agreed.

Very good practice to tie DC zero volts to ground. A floating power supply can do some really weird things, especially to analog signals.

I still remember THAT lesson from the school of hard knocks!
 
^ Agreed.

Very good practice to tie DC zero volts to ground. A floating power supply can do some really weird things, especially to analog signals.


Disagree, I don't ground the 24vdc common especially for analog devices because ground can be a very noisy environment.

There are systems that require a grounded common though. Such as ignition systems.

I went to a different school of hard knocks.

This has been talked about before. See link.

http://www.plctalk.net/qanda/showthread.php?t=23355&highlight=grounding+24vdc
 
Last edited:
Thanks for the answers so far..

I have ran into pressure transducers that would not work unless negative was grounded.

This is the procedure I use.....each PS has its own Positive and Negative. Even though the Negatives are grounded, I don't use a common negative for both PS.

You might say I treat the negative the same as the white neutral on 120VAC system.
 
we normally have 120V DC battery bank and 24VDC battery bank and both are floating.

Our latest job is using 120-24VDC converters instead of the 24VDC battery bank, with 24VDC- grounded, but still 120V DC is floating.

One nice thing about the floating DC supply is that it is possible to detect a single ground fault and fix it. two ground faults are required to blow a fuse.

It is an effort to make sure that none of the equipment internally grounds the DC- or to mount it in such a way as to keep it isolated.
 
Hi

I must have done to same school Of hard knocks as mickey as we never ground the common either. Must but not all panels I see would be the same but here anyway if you do the wire should be blue and white in colour and if you don't it should be just blue.

Donnchadh
 
Very good practice to tie DC zero volts to ground.
Careful, the only reason it measures "0 volts" is BECAUSE you tied it to ground. Otherwise it will measure -24 volts or -120 VDC, or whatever. Connecting (-) to ground does not mean that is is no longer negative relative to the + side of the power supply, but that it is no longer negative relative to your ground point. It is a hard lesson to learn, and a subtle point that is often missed.
 
Careful, the only reason it measures "0 volts" is BECAUSE you tied it to ground. Otherwise it will measure -24 volts or -120 VDC, or whatever. Connecting (-) to ground does not mean that is is no longer negative relative to the + side of the power supply, but that it is no longer negative relative to your ground point. It is a hard lesson to learn, and a subtle point that is often missed.


On ungrounded 24vdc systems if you use ground as a reference you would see
about 12vdc on the common or plus side. I do not use ground as a reference with a ungrounded system, I use the common of the 24vdc supply.

I have had electrians/technicans tell me they only have 12vdc from the power supply, I then ask what they are using for a reference.
I can't remember if you would see a negative 12vdc on the common side reference ground.
 
Last edited:

Similar Topics

Hello, hoping to get some feedback on this overnight. I have a couple of Omron FQ2 cameras connected to a 1763-BBB Micrologix & 1762-OB8...
Replies
2
Views
3,027
Hi everyone, I am currently working on a project designing a high speed envelope feeder and need some help hunting down the right PLC for the...
Replies
13
Views
4,665
I have been requested to test this proportioning valve for PLC control of flow/pressure. Dwyer Series SVP Proportioning Solenoid Valve The flow...
Replies
10
Views
425
We normally ground the -24VDC side of a control systems power supply. What are you folks thoughts about grounding the -24VDC side of a class 2...
Replies
1
Views
117
I have a conundrum with this current circuit. I have a Siemens 1215C AC/DC/Relay and an old drive - Ratiotrol (now Boston Gear company I...
Replies
7
Views
1,178
Back
Top Bottom