Here are some more points on the pros and cons of grounding DC negative
ken moore:
Sparky:
BobLfoot:
BobBBB -
Roy Matson
Curt Wuollet:
ken moore:
"Back in the day when we all used linear power supplies, the common was always grounded. Since we've moved on to switch mode power supplies, we always leave the common ungrounded, with a switched power supply you have true isolation. If you use NPN inputs, I recommend you NEVER ground the common"
Sparky:
"Safety - Most people think of 24VDC as safe (including myself) and have no problem touching anything with 24V. Now lets say, the common is not grounded and some where in the circuit a DC Cmmon wire comes in contact with a high voltage like 480V, a fuse will not blow nor a breaker trip. The next time someone touches +24VDC, they will find themselves in contact with anywhere from 300-500 Volts."
BobLfoot:
"I think we must distinguish between Controls DC and Instrumentation DC. In Cotnrols DC it makes a lot of sense to ground the 24 - for the reasons listed. In Instrumentation DC there are an equal number of arguments (isolation, noise, cross-talk) for not grounding either side of a 24 vdc supply. "
BobBBB -
"I work with genertaor systems all the time.
The battery supply negative is grounded - it supplies the hard wired stuff and generator controllers.
Secondary supply to the PLC is through a 24VDC/24VDC switch mode power supply. Negative is NEVER grounded, for isolation purposes. Battery chargers can go high, surges damage the PLC etc. The switch mode affords protection to the PLC but if the negative is grounded there is no isolation between one side of the switch mode and the other. May as well not use one.
Another reason for not grounding the negative to a PLC: - NPN inputs - grounding an input wire in the field can turn the input on - if it is not grounded there is no ground reference and the input will not inadvertently turn on. Typically found on Japanese machines. I normally use PNP inputs and do not really care if the output is NPN or PNP. Usually use NPN outputs."
Roy Matson
"If the negative is not grounded and the positive gets grounded by accident, no fuse will blow but all the signals that were floating around zero will now be at -24 which some input cards won't be able to read, i.e,. the signal input will be -23 to -19 instead of 1 to 5. If the card shares the power supply it's probably OK however quite often they are separate.
If the short to ground is only intermittent, it might be very hard to find the fault. wheras if you blow a fuse or pop a breaker on just the faulty loop, it's much easier to find"
Curt Wuollet:
"Pro grounding the DC negative: you won't get too far along before you hook up a piece of gear that ties the negative side to ground and that may be a bad place to ground for noise and ground loops. It makes chasing a problem a lot easier if you know where the ground is and you return everything within reason to that point."