AB compact logix
The layout is:
5069-l320er — 5069-IF8— 5069-IF8— 5069-OF8 — 5069-IA16 — 5069-OA16
The processor is 24vdc
There is SA power and mod power on the plc
I had someone hook up AC power to the SA power terminals (thinking of the ac input & ac output card)
Powered it up and POP.
I’m not getting any faults on the processor display
My card lights are solid green
My indicator in Studio 5000 show RUN (green) OK (green)I/O (green)
If I look at the card it doesn’t really show a fault
If I look at the CHANNEL on the card it says
FAULT EXISTS: YES
FIELD POEWER: NOT PRESENT
Rockwell says that if I applied 120 V to that as a power that the cards are fried.
ARE THESE CARDS garbage?
Is there any repairs to fix this blunder? Something to solder? Anything?
Allen Bradley shows none in stock until February
3rd party/ EBay stuff is way more than factory pricing, and seems risky.
ANY ADVICE is appreciated
Most likely they're dead. If you had a spare CPU, you could try the cards in a new racking.
I've never had much luck with 120v on 24v things, though some of the Finder relays lasted surprisingly long.
Send them to Radwell etc for repair. The cost will be 50% of the list price for a new card.
I wanted to circle back to this and say THANKS.
I sent them to Radwell based on your post and I am up and running.
I appreciate the recommendation.
Just curious - I see there are channel configurations for the 5069-IF modules that let me type in the high & low Engineering units as well as the...
1,002
Got a trouble call with a 5069-IF8 module that has all the channels flashing red. Upon logging in, I see that each channel is faulted with the...
3,086
Got a trouble call this AM from a customer saying they lost a level input. Looking at the input, I could see the signal was < 4mA, but not 0...
1,441
Hey Hive Mind, I am in the process of installing a L330ER with some 5069-IF8 IO cards. Some of my existing sensors are 3-wire 4-20mA. How are you...
5,384
I am getting some erratic behavior from this card. Channel data seems to be very erratic. This card is being used with the 5069-L330ER CPU...
2,396