5069-IF8 channel showing 3mA with nothing on it
phuz
Jun 2008
Mohnton, PA
1,044
Got a trouble call this AM from a customer saying they lost a level input. Looking at the input, I could see the signal was < 4mA, but not 0. Rescaling the channel engineering units to 4-20, I could see the input was a solid 3mA. They tried to feed 4-20 into the card, but no change. Moved to an open channel and all is well. What causes a channel to go into a state like that?
if it was faulted/broken and the configuration is set to default to specific input level, that would be my guess. It all depends on how it is set up.
you can see something about it here on page 49
https://literature.rockwellautomation.com/idc/groups/literature/documents/um/5069-um005_-en-p.pdf
If you're just talked about why a card would just fail, then any kind of surge can kill a loop input. I've had to switch over a few of them at pump stations that had been hit by lightning over a weekend. It fried wiring and fried the inputs.
Thanks, that's what I was looking for. Not sure what killed the channel, but it's dead. Didn't realize they clamped it at 3mA.
Just curious - I see there are channel configurations for the 5069-IF modules that let me type in the high & low Engineering units as well as the...
1,004
Got a trouble call with a 5069-IF8 module that has all the channels flashing red. Upon logging in, I see that each channel is faulted with the...
3,088
AB compact logix The layout is: 5069-l320er — 5069-IF8— 5069-IF8— 5069-OF8 — 5069-IA16 — 5069-OA16 The processor is 24vdc There is SA power...
1,865
Hey Hive Mind, I am in the process of installing a L330ER with some 5069-IF8 IO cards. Some of my existing sensors are 3-wire 4-20mA. How are you...
5,385
I am getting some erratic behavior from this card. Channel data seems to be very erratic. This card is being used with the 5069-L330ER CPU...
2,398