Got a trouble call with a 5069-IF8 module that has all the channels flashing red. Upon logging in, I see that each channel is faulted with the FieldPowerOff bit set to 1. I had them verify the SA power is good, which it is, and another 5069-IF8 module 2 slots down is functioning fine, so SA power appears to be good.
Module appears to be healthy otherwise. I haven't seen this type of failure before.
It certainly sounds as though the module is bad.
Can you remove the module and check for anything obvious like bent pens, etc? There may be internal fusing on the module that is opened, you may be able to open the case to find and replace it.
Phuz - did you ever find anything on this? I'm having the same problem. o_O
Were you able to find someone to repair the IF8? Also, would you update if you found anything? just curious if you had an I/O fault when this happen as well.
No I/O Faults.
As far as I know the customer never sent the module back for repair (no idea why)
Just curious - I see there are channel configurations for the 5069-IF modules that let me type in the high & low Engineering units as well as the...
1,004
AB compact logix The layout is: 5069-l320er — 5069-IF8— 5069-IF8— 5069-OF8 — 5069-IA16 — 5069-OA16 The processor is 24vdc There is SA power...
1,863
Got a trouble call this AM from a customer saying they lost a level input. Looking at the input, I could see the signal was < 4mA, but not 0...
1,441
Hey Hive Mind, I am in the process of installing a L330ER with some 5069-IF8 IO cards. Some of my existing sensors are 3-wire 4-20mA. How are you...
5,384
I am getting some erratic behavior from this card. Channel data seems to be very erratic. This card is being used with the 5069-L330ER CPU...
2,396