What is the difference between a Allen Bradley NT4 and a NI4 input card? I am using a NI4 card for temp, but what is the difference? Do I need a CJC with the NI4?
 
Last edited:
Yes I know I need a transmitter for the NI4 which I have, but what is the dif in relation to the NT4? Does the NT4 have its own transmitter built in to it?
 
You can connect a thermocouple directly to a 1746-NT4 card. Then configure it for the type of thermocouple you have. It will then give you a temperature value.

With the 1746-NI4 you will have to convert it's raw data to a temperature value
using math instructions or a scaling instruction. Advantage of the NI4 is you can use it for other inputs ( pressure,flow,level...) not just temperature.
 
Does the NT4 have its own transmitter built in to it?

That's one way to look at it. The NT4 card converts a millivolt value to a temperature value based on how you setup the card. Each type of thermocouple has it's own millivolt response to a given temperature, see chart below for different type of thermocouple responses.

millivolts_Temp.jpg
 
I have mine scaled to the transmitter range, is that correct or do I scale it to the thermocouple range?
 
I have mine scaled to the transmitter range, is that correct or do I scale it to the thermocouple range?


Have what scaled?

You have mentioned two different cards which one are you using?

Can you post your .RSS file ( zip it first) tell us the type of thermocouple.
And range you want.
 
If using a transmitter tell us how it is scaled ( e.g 4-20ma = 32 to 250 deg) or whatever.

Are you going to use this for control (PID)?
 
I'm using NI4, I'm using a K type thermocouple, and my transmitter is a 4-20ma, with a range of 0-600 degrees.

I set the min input to 3277 and the max input to 16384. when I set the scaled min to 0 I get a reading that is way off the current temp.


Is there some other math I have to add into this the get what I need?

What determines how it is scaled to?
 
Based on the info provided see picture below for a typical scaling program.

Post your .RSS file and someone can take a look ( zip it first)

You might want to check the milliamp value to make sure the transmitter is giving you an accurate curent for a given temp.

ScaledValue.jpg
 
What determines how it is scaled to?

Not sure I completely understand the question.

Raw data from the card depends on the input. See picture below. Scaling depends on what the analog input represents. In your case you said 0-600 deg.

Is the card setup for current? Check it's dip switch.

RawData.jpg
 
that is exactly what I got, but isnt the f8:0 supposed to read me the temp or is there more math?


Yup it should be temp.

What are you getting?

What is the raw data value?

What is the milliamp value?
 
Last edited:
Still trying to figure out how to make a copy of the program, but it is EXACTLY the same as the you posted.

But for the output I am getting in the range of 0.90000 to 1.60000.
My transmitter is definitly a 4-20ma, I even looked it up to make sure at the manufactors sight.
My thermocouple is a K type for sure.

I did manage to get it real accurate when I put the scaled minimum to 80.6 then it would only be off a few 10ths in the whole range.

What else could it be? Maybe it is readindg celseis? (metric)
 
Last edited:
Sounds like the scaling of your transmitter is not 0-600 deg F. I would double check it
if you have the equipment.
Also if you have a milliamp source then connect that to the PLC and check the PLC's response.

Maybe it is readindg celseis?

Could be.. 0- 600 deg C = 32-1112 deg F (change the Scaled min and scaled max to 32-1112 and see if that looks right, you can always change it back).
 
Last edited:

Similar Topics

I am having an issue getting a IY4 to read my thermocouple correctly. We have a R type and K type hooked up and sitting at a known room...
Replies
5
Views
540
Posted by u/mr_biodtox 44 minutes ago Delta ISPSoft - Establishing communication with thermocouple module Hi, How do I establish communication...
Replies
1
Views
341
Hi, We have an ongoing project with a lot of thermocouple involved that monitor the temperature of heaters. There are more than 20 PID...
Replies
32
Views
3,489
Hello. PLC beginner here, so apologies in advance for any incorrect terminology or poor communication. I have an SLC 500 Thermocouple/mV Analog...
Replies
1
Views
652
Hello Guys, Trying to scale a thermocouple directly into my IY4 card. Connected into the terminal +\-. I’ve scaled the range of my J type to...
Replies
4
Views
1,677
Back
Top Bottom