OUT (C)
(1) When the operation result of the instructions preceding the OUT instruction
have changed from OFF to ON, 1 is added to the present value (count value).
When the counter has counted out (counted value = set value), the state of the
contact is as indicated below.
NO contact Continuity
NC contact Non-continuity
(2) When the operation result of the instructions preceding the OUT instruction
remain on, counting is not performed. (It is not necessary to convert the count
input into a pulse.)
(3) After the counter has counted out, the count value and the status of contact do
not change until the RST instruction is executed.
(4) If C256 to C1023 are used with the AnA, A2AS, AnU, QCPU-A (A Mode) and
A2USH board, specify set values as described in Section 3.8.3.
(5) A negative number (-32768 to -1) cannot be used as a set value. When the set
value is 0, the same processing as for 1 is performed.
(6) For the counting process of counters, refer to the ACPU Programming Manual
(Fundamentals).