AB DeviceNet
hazey
May 2003
Australia
73
Hi guys looking for some help. I have a Controllogix 1756-l55 ver 11.25. It currently has a 1756-dnb ver 3.01 card installed. I have installed another scanner card ver7.01. The problem is with this card I can see it in RSWho but cannot connect to it. Also have field devices connected with an error on card of NO RX (no scan list?) The card has a mismatch error when looking at properties in RSLogix. Do I need to change firmware of 1756-dnb to 3.01? I have controlflash but when I try to do this I cannot see any revisions when I click show all?
Thanks for your help
Hazey
RSLinx 2.42 and RSNetworx ver 5. I do not want to upgrade the old card I just need to get the new version working.
thanks
Hazey
What files is controlflash looking foe? EDS? I seem to have the firmware upgrades but they do not pop up on screen?
thanks
Hazey
RSLinx is showing the card with no question mark. The original card has a plus symbol beside it, when you open that there is another tree with A DeviceNet. The new card does not have this tree???
thanks
Hazey
hazey said:
Thanks Praveen. Download it into RSnetworx?
thanks
Hazey
Download it onto your pc somewhere and then use the RSLinx EDS Install tool to install it
hazy,
a mismatch error is telling you that one of your devices in the real world is not a match for the device in the DNB's scan list. mismatch can include a devices revision level. example:
powerflex40.rev4.03 in scanlist
powerflex40.rev4.01 is real world
another example:
powerflex4.rev4.03 in real world
depending whether you have selected to ignore minor revision mismatch or not will determine if your network scanner will remain in communication with the mismacthed device.
Hope this helps.
BD
RSL5K ver 15 only support DNB 7.01 so disable the keying will solve the issue
warning!!!
Disable the keying causes the processor will issue commands whatever the module place in the paricular slot based on logix so be beware the safety issue
Bikerdude at this stage I have no scanlist in card as I cannot download into it. The error is there with cable disconnected.
thanks
Hazey
Praveen I had disabled keying as an earlier thought but It did not help. I will need to try eds file in the morning.
thanks
Hazey
Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
65
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
179
Hi, I am looking to migrate some of our Electronic Overloads off of a Troublesome Devicenet Segment. Is there any documentation confirming the...
144
We've run into an old system that we are upgrading which is still running Steeplechase with Citect using Devicenet to Wago. I had some experience...
165
Sigh, DeviceNet noob... I have a 1756-L55, with a DeviceNet module, and 10 PF700 all commanded with DeviceNet. One of the PF700's blew up...
152