We have an ArmorStart Distributed Motor Controller (284G-FVD7P6D-25-RRG-CBG-DB1-EMI). It is used to run an Over Head Lift motor on a Hoist. One day someone disconnected the Motor Power Cord Connector at the Motor (which is on a platform about 15 feet off the ground). I did not know the power feed to motor was disconnected. The Hoist was in the UP position and holding a Car. When I went to the HMI screen and retracted the “Locking Pins” and then selected “Manual Lower Hoist” the ArmorStart Controller released the Brake and with no torque / voltage on the Motor (motor power feed disconnected @ motor) gravity brought the Car speedily down (about a five foot drop). The Lift’s wire cable unspooled from the Lifter’s Drum and did some other minor damage to Car and tooling.
I do not, ever, want this to happen again.
My thought is I do not want to release the brake when there is zero voltage applied to the Motor. I was thinking of adding a relay at the pecker head of the Motor and interlock the brake through this relay. In other words if the Motor is not energized the contacts on the relay will be open and the 120v brake cannot energize and release. My problem is I do not know if this is possible with this VFD driven Motor. The motor is a 480V AC Motor. Would a 480 volt relay work on what I think is PW modulated VFD voltage to motor?
Any suggestions or thoughts? Is this a proper application for this type of AmorStart Controller? I feel something is wrong here because this should be engineered so the above mentioned cannot happen.
See page 42 & page 43 of the "ArmorStart Distributed Motor Controller Application Guide" for a simple diagram.
https://rockwellautomation.custhelp.com/ci/fattach/get/114920/
I do not, ever, want this to happen again.
My thought is I do not want to release the brake when there is zero voltage applied to the Motor. I was thinking of adding a relay at the pecker head of the Motor and interlock the brake through this relay. In other words if the Motor is not energized the contacts on the relay will be open and the 120v brake cannot energize and release. My problem is I do not know if this is possible with this VFD driven Motor. The motor is a 480V AC Motor. Would a 480 volt relay work on what I think is PW modulated VFD voltage to motor?
Any suggestions or thoughts? Is this a proper application for this type of AmorStart Controller? I feel something is wrong here because this should be engineered so the above mentioned cannot happen.
See page 42 & page 43 of the "ArmorStart Distributed Motor Controller Application Guide" for a simple diagram.
https://rockwellautomation.custhelp.com/ci/fattach/get/114920/