Can 24VDC NPN Output, switch a 12VDC Relay?
ndzied1
Aug 2002
Chicago, Illinois
2,857
So long as the commons are tied together and the current is not overdrawn, can I use a 24VDC NPN output (sinking) to switch a 12VDC Relay?
So one leg of the relay coil is tied to +12VDC and the other leg wired to the NPN output?
Thanks,
I don't see why not, and i don't see what harm it would do to try it.
But why not use a 24V relay, or are times really that hard ?
I have been requested to test this proportioning valve for PLC control of flow/pressure. Dwyer Series SVP Proportioning Solenoid Valve The flow...
450
We normally ground the -24VDC side of a control systems power supply. What are you folks thoughts about grounding the -24VDC side of a class 2...
133
I have begun using 480VAC power supplies in my panels to keep heat from a transformer out of the panel. This works great if the panel is mounted...
17
4,190
Good morning, could anyone recommend a 24VDC pulse counter which counts up or down to a preset #? Once it reaches this number, send a 24VDC back...
1,670
UL 508: Any reason I can't supply a 60W 24VDC power supply from 2 legs of 480VAC? Our MechE is asking, it is for a product I don't deal with. My...
5,901