I use WINCC Flexible 2008 with 2 PLC CPU 315-DP in a software redundacy configuration. I can configure 2 Connection for 2 CPUs but my tag can address only one connection at a time. How is it possible to maintain the connection if other CPU becomes master. If all my tag address connection1 what happens when connection1 fails and connection2 takes over. how could i solve this problem
Regards
RTA
You could do it sorta how the guys who do 400-H systems handle the change connection function.
PLC_1 is a connection, PLC_2 is a connection and the tags and everything in WinCC reference a separate connection named PLC_Changer or something. My biggest problem I've found in doing this is that you lose your ability to do symbols in WinCC.
You dont have to use FB523 when using software redundancy. You can use the status word to know which station (A or B) is the master. The status word is DBW8 of the Instance db for FB101.
If the instance DB for FB101 is DB101 then the bit DB101.DBX9.0 is TRUE when the station is master.
You can configure the PLC connection tag to change connection when this tag is TRUE as in the example on the siemens support Forum.
Thanks Rohan
The point here is the tag can have only one connection , so as long as A is master the tag communicates to connection1 but when when B becomes master the tag losses its communication as A goes to standby
Regards
RTA
RTA,
I think you missed the point, there are three connections say CPU A, CPU B and CPUAB in your WinCC Flex project. All the tags are connected to CPU AB which is a dummy.
You utilise the 'Change connection' function to switch the connection of CPU AB to the master CPU which maybe CPU A or CPU B.
The status words are monitored by two tags to trigger the 'Change connections' function. The FAQ illustrates this with an example for S7 400H.
Thanks all,
I have tried as per the link mentioned by jesper.
I have uses the limit to invoke the change connection function
but the address change does not take place
I also tried with db5.dbx9.5 redundancy link failure and db5.dbx9.0
both are not able to change the connection to the current active CPU
What is that i am missing
Thanks for all ur help
Have you set the acquistion mode for the tags to 'Cyclic Continous' instead of 'Cyclic on use'?
I can send you a small program where this function is used if you send me your email id as PM.
Thanks Rohan for Ur kind support
I could take care of the changeover by the method mentioned in the FAQ with a little modification
I use 2 CPUs with address 2 and 3 , when monitoring the db5.dbb9 of the CPUs i could find that CPU with the address 2 was active the values of DB5.DBB9 was 5 and 10 and when CPU with address 3 was active DB5.DBB9 was 6 and 9 so played with limits of the tag
Now there is no problem, the changeover works very fine.
Once again i thank u for your kind support
Keep the good work going.
Regards
RTA
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
303
Hi all, I am having an issue where some of my HMI push Buttons and Indicators go in to error when I navigate to a new screen. I am using a...
567
We have a new machine that uses an armor block to transfer input signals for conveyor position that continuously alarms out on no position change...
114
Hello everyone, I am trying to change the IP address of the Omron PLC (NJ30-1200) and HMI (NB7W-TW01B) to fetch the network on our network...
325
Dear Experts, I'm just started working with GEO SCADA and I need your valuable help. Currently, I'm trying to edit the alarm limits on MIMIC...
239