CHANGING FROM REMOTE-RUN TO PROGRAM MODE WITH THE KEYSWITCH on a ControlLogix L73

NotEinstein

Member
Join Date
Feb 2020
Location
NWT
Posts
4
Hi,
I am curious to know what will happen to a Running 1756 ControlLogix L73 controller if the keyswitch is changed from Remote Run to Program Mode while online
 
Welcome to the PLCTalk forum community !

The short answer is: "The controller will go into Program Mode".

The Continuous Task will execute the remaining un-executed Programs for this scan cycle, then stop.

The controller will not execute any more Periodic or Event tasks.

The controller will send Program Mode state messages to all active I/O connections. Most output connections go to OFF or zero outputs, and most VFDs fault or stop, when you go to Program Mode.

The controller will go into Program Mode and wait. You can perform edits, make nonvolatile memory save/restore actions, or just leave the controller idling.
 
Do some in-depth research and make sure you understand what it "will" do.

As Ken said most physical outputs turn off and most drives fault but this is not always the case.

For example, on many of the 1756 series output cards, you can choose what state the outputs go to when in program mode and when the controller faults.

This can be selected on an individual or a group basis in most output modules.

In other words, some outputs that were not on during run mode could turn on when switched to program mode depending on how it's set up and depending what the output is wired to this could be dangerous so just something to double-check.

These options can be set programmatically or with the RS Logix 5000 or Studio 5000 software packages.
 

Similar Topics

Good morning all. I looked through previous posts and didn't find any help on my exact problem. I have a 1769-L33ER PLC running a water jet...
Replies
4
Views
1,862
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
236
Hi all, I am having an issue where some of my HMI push Buttons and Indicators go in to error when I navigate to a new screen. I am using a...
Replies
16
Views
471
We have a new machine that uses an armor block to transfer input signals for conveyor position that continuously alarms out on no position change...
Replies
0
Views
90
Hello everyone, I am trying to change the IP address of the Omron PLC (NJ30-1200) and HMI (NB7W-TW01B) to fetch the network on our network...
Replies
7
Views
289
Back
Top Bottom