CLX DLR with ETAP-1F??
cardosocea
Nov 2016
Fields of corn
2,642
Hello,
I have an application where I want to make a DLR where part is done in Fibre (using the Flex5000 SFP adapters, ETAP-2F for 1719 IO racks and an EN2TR card.
From other rings, usually you have to go from port 1 to port 2 and vice versa, but that seems to be impossible to do on the ETAP-1F since Port 1 is always Copper and 2 is fibre.
The other doubt I have is where the ETAP is to behave as a copper-fibre converter, which RJ45 would I use? The link port? Or the device port? Sadly, Rockwell documentation isn't very forthocoming on this.
Hello. I have worked with DLR in RJ45 only, but it seems to be possible to mix media for DLR as explained here. My only word of caution is to use the ETAPs as DLR node, because at least the ones that I have (which are very old) support only version 3 of the DLR object. Anyways the Flex5000 are relatively new devices and support DLR supervisor. You can check the version of the DLR object with the ODVA/Molex tools. If it is version 3, then use them as DLR nodes only; this would be my advice.
I was wrong about the revision number of the DLR object but correct in the sense that the revision for the ETAP (Rev 2) is older than the revision for newer devices such as 5069-AENTR/A (Rev 3).
Controller: 1756-L84E v.35 Prosoft MVI56E-MNETC for ModbusTCP/IP I'm having an issue with some of my write commands. The write command that...
198
I have several Avery scale units and they are configured as Generic Ethernet modules, and I am actually reading the data fine for the weight...
424
What's the best way to move a tag value from the panelview+7 to the clx plc. We display amps from a power meter on the panelview screen, read in...
400
I'm running into an issue migrating a PLC-5 using the newer Logix Designer Export when opening a saved .ACD from RSLogix-5. It has multiple RIO...
621
We have two sites that are stranded with no line of site, they are handled by phone/modem with a chain that includes: Stranded site (client)...
912