I haven't been able to find any examples of CompactLogix (DF1) to 1770-KF2 to SLC 5/04 (DH+) message instructions.
Anyone able to achieve this? I only want to be able to read.
I have it all connected.
I can see the 5/04 through my laptop via serial cable.
Problem I'm having is for the message instruction.
I have my path set as 2, 0
Communication method is CIP.
I don't get an error when it triggers, but don't get a down either.
Anyone care to take a guess.
Processor has correct serial settings, (Same as laptop)
Got it
Path is 2, 1
Message type is PLC5 Read (or Write if I had to, but I'm only reading)
I guess I thought it was more complicated then it ended up being.
Got it
Path is 2, 1
And based on the responses, you are probably the only one who has done this ( your exact setup). ( or one of a very few)
That KF2 box is getting pretty old now. I have seen one working for the last 18 years now without a hiccup.
Maybe I should post all results in case someone else tries this.
Next I will try 2 slc 5/04's on it.
I only wish this would work with an ENI module.
The knowledgebase was kind enough to state it was possible, but no example.
Even better, I can map through the compactlogix processor to go online with the 5/04. Seems pretty good at 9600 baud.
Controller: 1756-L84E v.35 Prosoft MVI56E-MNETC for ModbusTCP/IP I'm having an issue with some of my write commands. The write command that...
210
I have several Avery scale units and they are configured as Generic Ethernet modules, and I am actually reading the data fine for the weight...
444
What's the best way to move a tag value from the panelview+7 to the clx plc. We display amps from a power meter on the panelview screen, read in...
406
I'm running into an issue migrating a PLC-5 using the newer Logix Designer Export when opening a saved .ACD from RSLogix-5. It has multiple RIO...
638
We have two sites that are stranded with no line of site, they are handled by phone/modem with a chain that includes: Stranded site (client)...
925