CMore scrolling alarms
Dariusincj
Jul 2011
Missouri
43
I'm trying to figure out the best way to scroll through multiple alarms if multiple alarms are present. I have a CMore connected to a SLC504. I have an integer, lets say N7:100 and this integer is wrote a 0-4, 0 being no alarm, 1-4 being alarm a-d. I'm unsure on how to program N7:100 to switch between alarm 1-4 if more than 1 alarm is present. I thought about using a FIFO but unsure about that as well. Any suggestions?
I use a multi-state text indicator on a background screen so I can have more customization of size/location of the alarm banner on my Cmore products.
The tricky part would just be how long and how you want to cycle through your multiple alarms. It For only 4 alarms it wouldn't take much logic to hold each alarm for a moment before resetting the message hold and allowing the next one to overcome. I usually have about 100 or so alarms/messages, so I just set a priority in my logic (Faults -> Alarms -> Warnings -> Status Messages) and display one at a time with the more important message taking priority.
What you'd want to do is pause or hold the N7:100 for a short time before moving the next fault/alarm message number into the file, so that the Cmore will display the previous message before overwriting it with the next.
I can think of some quick and dirty ways to do it that involves some Latches/Unlatches (or seal ins, if that is your preferred method) and Timers per alarm rung. When checking for Alarm 1, set a latch that will delay Alarm 2 for X time and not allow Alarm 1 to be set again until the end of the checks (or do not set it if Alarm 1 is not true), then Alarm 2 would delay Alarm 3, 3 delays 4, etc. Last alarm check would reset the loop and allow Alarm 1 to be set again. If no alarm is set, the delay time is zero. If the alarm is set, the delay time is what ever your desired alarm display is (2, 3, 4, seconds, etc.)
Hi everyone, recently i worked with a cmore panel and have the question that how can clear alarm list whit remote form,right now only can with...
132
Hello, I am new here and have been working with PLCs for a few years now. I have been tasked with setting up a Micrologix 1400….. to a Cmore 10...
551
I working on installing a EA9-RHMI so I can use a TV screen for my HMI. I wanted to be able to show multiple screens on the TV at one time, but...
1,350
I am stumped here. Anytime I put the PLC into run mode the HMI comes back with PLC-497: error code 0x010100 returned from PLC on CIP and also...
2,035
I have a program that set the speed for a VFD via an 0-10v analog signal signal . I am trying to read the analog signal from the VFD to the HMI, I...
853