Compactlogix L32E Date/Time Issue
CAAJ
Dec 2014
Fairhaven, Ma
47
Hello All,
I am having a problem on my controller with Date/Time where these values seems to float away from the actual Date/Time. Is there any way to prevent the PLC's Date/Time parameters from floating? Is there maybe a way where I could sync the PLC to the desktop Date/Time?
Any feedback would be much appreciated.
Thank you
CAAJ
:D
Clock drift is a problem with any computer system. We don't notice it in the modern Internet-connected world, but with an embedded system that's subject to wide temperature swings, oscillator drift always causes clock drift.
The most common way to handle it is the Logix 5000 Clock Update Tool. This runs on a server or workstation PC that's connected to your automation network and also has a connection to a real-world time server (whether internal to your network, or out on the Internet).
The Clock Update Tool then sends the current time down to controllers periodically, based on a schedule you configure.
That tool is an installation option for Logix 5000, and is on the RA Knowledgebase (well, it's probably in the RA Knowledgebase, which has been having some infrastructure problems this week).
Thank you Ken,
I have downloaded the tool and I am now able to add my devices which I need to synchronize, however when trying to sync I receive an error which states "Failed to synchronize device, please check connection". Is this a software bug? I'm running windows 7 and utilizing version 2.4.0 of the tool. Or have I not configured the tool properly?
Thank you Ken,
It is hard not to configure the tool properly...
"check connection", in RA Speak, infers that the tool cannot "see" the device, but since you add devices using RSLinx's browser, I can't see how you can get it wrong.
Thought I'd try it myself, I've got a 1756-L62 in slot 1, a 1756-L63 in slot 4, and an old 1756-L1 in slot 5.
The only one that the tool succesfully synchronises is the old 5550, and I get the same errors as you on the L6x controllers.
Older versions of the Logix 5000 Clock Update Tool are not supported on Windows 7 32-bit or 64-bit. For Windows 7 you should be using at least version 2.5.0 of the tool. Support was specifically added for this environment with this version.
You can download the latest version of the tool for free here...
44321 - Logix5000 Clock Update Tool
Access Level: Everyone
v2.5.2 is the latest available from there, at the time of writing.
Regards,
George
Regards,
George
Yes, that sorted that problem... thanks George
EDIT : can't modify the Event Start Time - just keep getting "Unspecified Error". I was thinking that if you had something like hourly reports to compile, you would want to synchronise clocks just before the hour, so tried setting the Event Start time to XX:59:59 (1 second before the "hour"), error - tried other times - error... etc., etc.
Good stuff. Thanks for checking Dave.
Geospark Clock Update Tool: 1:00am!
Bedtime methinks?
26 port Stratix 8000, PACs, PV5500, AENTRs, bunch of PF525s all waiting for me in the now morning! Oh it's shutdown week alright.
Cannot wait...
Night...G.
Hello All,
After downloading the latest version I am now getting an error when opening the tool that says, "The program can't start because mfc100.dll is missing from your computer. Try reinstalling the program to fix this problem". Even after repairing/reinstalling, same error continues to arise. Has anyone experienced this issue, and if so, is there a fix?
Thank you
CAAJ
This appears to be related to Microsoft Visual C++ 2010. The mfc100.dll file belongs to this software...
554413 - Clock Update Tool is giving an error with mfc100.dll
Access Level: TechConnect
You need to install or reinstall Microsoft Visual C++ 2010 Redistributable Package as per the technote above. This should hopefully solve your issue.
Regards,
George
I have a customer that has asked me why when power is cycled to his Compactlogix he loses the date and time and he has to go back in and set it...
9,720
Hello . Info: Panelview plus 400 2711P-K4M20D Compactlogix 1769-l32E i make a program in RSlogix 5000 and Factorytalk view for...
1,819
Hello again. I need to flash a CompactLogix L32E from firmware ver15 to 16. It has several Panelview Plus's Series D Rev A, connected via...
2,802
Hello. I am trying to establish communication between CompactLogix 1769-L32E and CompactLogix 1768-L43 using serial port but with DeviceNet (and...
2,778
Respected sir/madam I have CompactLogix L32E And I want to data log into logic . is any module or card require to it. request you guid me and if...
1,403