control logix 1756-l55 - Mitsubishi f940got
resin14
May 2009
ny
I have the service edition of rslogix 5000. A ranger robot has version 11.32 on the plc. 11.32 is not supported by service edition. Only version 12 and above. The PLC lost the proram and I have a copy of the original.I flashed the plc and the analog card to 15.5 and 15.1 respectively. I updated the file to version 15. Now the Mitsubishi HMI has a comunication error. I have tried different df1 serial/protocol but cannot get a connection. I tried the pendant on another unit and the pendant works. I have a service edition for the mitsubishi and have not been able to upload the program. I made a cable but still having trouble there. Thought if I new the communication setup of the f940 I might be able to comunicate and then set the PLC accordinally.
Ranger does have use version 15 with the newer GOT 1000 HMI. Ranger says programs are not compatiable with the 940. And there is no way version 15 will work with F940
It took techconnect 4 days of phone calls before I talked with a software engineer to tell me the 11.32 was not supported by service edition. i couldn't load ver 11
My question. Why would changing the version level change the communication. When I use RSlinx DF1 i have to configure with half duplex (version 15) I can't see how the version 11.32 communication is setup because the service edition doesn't
support 11.32.
Is there any way around this without purchasing rslogix standard edition so I can reflash back to 11.32
I have am trying to determine if I can use a 1756-IB16I (or some dc input equivalent) to handle a 24vdc input pulse frequency of 80 pulses per...
943
Folks, Putting together a system utilizing a Control Logix Gen 8 (5580) PLC w/ the L83e CPU. I'll be connecting to 8 different FLEX-IO drops...
4,110
Good morning. This is something new to me. we have an existing controller running one of our plants. we are doing a conversion on another...
1,260
As the title suggests, I'm pretty new to control logix. Well, what I am supposed to do is connect like 8-2 wire analog sensors to this card. From...
1,670
Good Morning , We had to change out a L61 with a L71 processor and it seems like our motion control is not the same . Have any of you run...
1,854