Control logix HSC module problem?
huynt
Nov 2004
106
Dear Sirs,
We have a system includes Oval Flow meter that gennerates pulses + A-B ControlLogix with HSC to count that pulses.
The problem is that, the amount of pulses that HSC counted from
Flowmeter is not equal to the real amount of pulses generated by flowmeter. We are afraid of noise or signal reduced by wirring, we try to test with a counter (Ormron H7HP – C8D), that counts correctly.
HSC produces greater amount, but sometimes less than the real value provided by flowmeter.
Please tell us any notice or experience of using HSC and HSCE. We met problem with both HSC and HSCE.
We are very nervous about this problem. Please reply ASAP.
Thank you.
What mode is the card set up for, what is connected to the Z input, what kind of wire are you using, where is the drain/shield terminated?
I have am trying to determine if I can use a 1756-IB16I (or some dc input equivalent) to handle a 24vdc input pulse frequency of 80 pulses per...
938
261
hi all, i have a plc i need to get info from for a site im working on: I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im...
383
I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
766
Possible for two processors in same rack to have separate motion groups across a single Kinetix Rack using a single EN3TR? One 6500/5700 rack, 8...
428