Hi folks
I would like to know, if there is an inexpensive method to contol an analog valve using a potentiometer and some kind of basic 4-20ma current generator.
 
With or without the use of a PLC?

You have everything that most don't already, as it would seem.
If you have the Analog Valve....which is usually the most expensive.....you can directly wire a PS with the rated output through the POT to the incoming 4-20mA input of the valve.

This is NOT normally the way you would accomplish a normal controlled sequence of an analog valve. Use one of the many profile controllers on the market....FESTO, HyDraulik-Ring, Parker...the list goes on.....

You need to be more descriptive about what you are attempting to do in order to make a real-life reccommendation.
 

Similar Topics

I have been requested to test this proportioning valve for PLC control of flow/pressure. Dwyer Series SVP Proportioning Solenoid Valve The flow...
Replies
10
Views
426
So I'm pretty green when it comes to troubleshooting in the field so bear with me. We have a Danfoss valve that opens/closes from an analog output...
Replies
23
Views
975
Hi there, We have a system at a water treatment plant where large raw water tanks feed into the plant that's all on the same level. At high tank...
Replies
18
Views
3,781
Working on a site where they are using a DeltaV DCS system. They are using Topworx DVC6200 controllers on their modulating valves. These control...
Replies
1
Views
1,075
Does anyone have any experience in this? I have a lead lag pump setup for water that is maintained by pressure using VFDS, the idea is to have...
Replies
6
Views
1,844
Back
Top Bottom