So I am working with a PLC5/40C Rev. A and a PLC5/40C Rev. C communicating through controlnet. The system is already setup and running. There is a integer file from one plc that communicates 8 words N74:200-N74:207 to N73:40-N73:47 of the other plc. I am seeing this in rsnetworx “scanlist configuration”. I have not worked with controlnet at all. I understand how the data flows from one plc to the other. My question is how do I transfer more data back and forth to the same plc’s? Do I have to modify the network schedule or can I do it in the plc program like controllogix msg system. Thanks for any advice.
You would have to re-define the Produced/Consumed data connection and re-schedule the ControlNet to increase the size of that scheduled data connection (or to create a new one).
You can exchange data between the PLC-5C controllers over the ControlNet with MSG instructions as well, but of course it won't be as fast and reliable as the scheduled I/O connections.
Thanks Ken! I do have the controlnet file and I can open it up in rsnetworx. I don’t have an experience with configuring it to add more data exchange between the two processors. I do however think that the message instruction is a good idea! I have done it many times on control logix platforms but not on PLC5’s. The data isn’t controlling anything just displaying information on a PV. Thanks
Similar Topics
Hello! I am working on a Controllogix project with redundant PLCs. The primary and secondary racks both contain: [0]L71 [1]EN2T [2]CN2R [3]CN2R...
Replies
1
Views
1,825
We have 3 control logix(7 slot) racks . Configuration is as follows Rack 1: P/S , CPU(L61),1756-enbt,1756-cnbr Rack 2: P/S , 1756-cnbr , DI , DI...
Replies
8
Views
2,716
Hey everyone, looking for advice in this particular scenario. Currently we have a controlnet bus that has (6) CN2DN devices and (2) powerflex...
Replies
5
Views
227
Does anyone know of a cheap USB to ControlNet or USB to DeviceNet adapter (I'm looking for both). I thought PLC Cable would have one but I did not...
Replies
16
Views
2,325
I'm having an issue trying to backup a ControlNet network. Within RSLogix5000, when I click on Module Properties of the 1756-CNB (Rev 5.001), the...
Replies
2
Views
877
Back
Top Bottom