shanmu_gam
Member
I have a siemens CP340 communicating with Prosoft ADM module and if sometimes by anycause if the PLC goes to stop mode and comes back RUN mode, the communication is not getting established. I have to download the hardware configuration again or reset the EN_R in FB2 P_RCV and set back the EN_R in FB2 P_RCV. Is there anyway to initialise the CP340 module while it come to RUN mode? Thanks