Danfoss VLT2800 output unplugged

HI

@Jeebs: Yes I see, to both my questions :)

@bornwild: It will depend on the brand, and what kind of money you want to pay. The VLT2800 is "old" technology, but even then they had the option to put in current transducers in the output. So buy a cheap drive and you'll probably not be able to trust the current reading.
But keep in mind that the theoretical calculation is not a fictional one. It is based on the DC current in the DC-link but influenced by the motor data including the motor magnetization current, and if these data are not correct then the calculation will also be incorrect.

As to your clamp meter, remember that you are meassuring on a current that is NOT a 50 or 60 Hz current. Your meter will be correct at one of those frequencies, but on the switched motor current of a VFD the result will be different. So if I were you I'd still rely on the value from the VFD.

Best regards,

Michal_dk
 

Similar Topics

Anyone experience with RS485 communication between an S7-214CPU and a Danfoss VLT2800?
Replies
1
Views
1,555
hi guys, i'm having a problem with this VLT2800, it is sending to me an "error 15" i need help. (im from chile, and the technical assistance from...
Replies
6
Views
4,376
not strictly a plc question, but wondered if anyone could help, i want to connect my laptop usb or serial port to a rs485 port on a danfoss...
Replies
7
Views
5,784
  • Poll
:furi::hand::smas:I HAVE TO INSTALL A DANFOSS VFD VLT2800 SERIES TO CONTROL THE SPEED OF FEED WATER PUMP TO MAINT THE 5 BAR PRESSURE IN LINE. MY...
Replies
3
Views
5,174
Is it possible to program the parameters of an Danfoss VLT2800 over a profibus network? And if so how can this be done?
Replies
2
Views
6,714
Back
Top Bottom