Devicenet Config with Schnieder MCC I/O
radar
Aug 2005
Florida
I am attempting to configure a Devicent 1747-SDN offline to communicate with a SquareD MCC. The MCC is using TSX Momentum 170 ADM 540 80 6point in / 3 point out modules with a 170 LNT 710 00 Devicent adapter.
According to all that I can find out from Schnieder, each of these small I/O racks is calling for 32 bytes in and out for polled data, which appears to force you to use Modbus and waste discrete and M memory to set it up.
Has anyone had experience with this, just wondering if I have to use all of this memory for a few I/O points, or maybe it will allow something different when online ???
Is the adapter a badged AnyBus device? i.e. a DeviceNet to ModBus gateway?
I had some unhappy experience with one of those interfacing to Telemecanique (Schneider) combo starters. As long as you used the default config for 8 starters and actually had 8 connected, it worked fine (32 bytes in/out). Had to jump through many hoops to get it to accept any config other than default (for less than 8 starters) and even then it was extremely flakey. Even trying to restore the default config was difficult.
From what little information I have gathered specific to the adapter, it appears that it only offers connectivity since all of the I/O modules detail a Modbus communication style. I was hopefull that I might be reading this wrong, but afraid it is exactly as you had done with a Devicenet connection to a modbus communication scheme, what a waste of scanner memory ! Thanks.
This is what the thing I worked with looks like.
Gerry,
Appreciate the reply, finally found out that this module happens to have a port for Modbus Messaging or Mastering, and therefore requires the 16 words in and out to set up Modbus, even if you don't use it.
Would it not be beneficial to you just to remove the momentum and install a AB product..I know it sound silly but the time wasted trying to make it work would probably offset the cost of a new controller..
D
Need some clarification regarding the devicenet set up PLC is CLX with 1756-DNB scanner, trunkline using kwiklink flat cable with the micro...
5,167
Looking for help in configuring explicit messaging in the RSLogix 5000 for devicenet 1336 drive is 16bit and current devicenet is mapped this...
3,217
Hi, The point io AO card OE2C will not take any output value. It also resets its configuration (edited in RSNetworkx for DeviceNet) every time...
3,218
Hello, It is possible to configure Flex I/O ( 1794 series ) by Passthru Ethernet to DeviceNet. I got this error list . What I made wrong. Any idias?
4,181
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
27