Devicenet Passthru
daviper1996
Jun 2010
roseville
I am attempting to configure devicenet passthru using my 1784-U2DHP cable to a SLC 5/04. I am able to add the Devicenet Driver 1747-SDNTP point to the appropriate SLC and everything seems to check out. However I am unable to actually browse the devices. I checked the Devicenet scanner and its M0/M1 is set to 395.
Any advice about what I am missing would be appreciated.
The SDNPT driver can be tricky; what firmware revision do you have in the 1747-SDN ? My recollection is that 4.015 was the minimum, and 6.002 worked well.
You also have to cycle run/prog/run at least once after downloading a configuration with the correct M-file size, to allow SDNPT to work.
It finds the correct slot for the devicenet scanner etc. Says it is running and all is well... However no devices show up. I did not have to set the file size as it was already there. I did cycle anyway.
How do I determine the firmware Rev. for the scanner?
When I go into Driver Diagnostic in RSLogix I can see that Interface Revision reads as 3.00 but is that the firmware of the Card or the Driver?
It probably is at 3.0; as Ken stated you will need a minimum of 4.015.
The 1747-SDN Firmware Revision Level is also stored within RSNetWorx for DeviceNet application file under the respective node's Properties.
I was trying to create the DNT file as I do not have one. Another vendor currently onsite has the Devicenet cable and we just finished replacing 4 drives. I will get with him and see about upgrading the firmware.
Thank you.
I read Ken's other post about configuration going well but no browsing but I am hoping this is a simple firmware issue.
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
22
Hi, I am looking to migrate some of our Electronic Overloads off of a Troublesome Devicenet Segment. Is there any documentation confirming the...
116
We've run into an old system that we are upgrading which is still running Steeplechase with Citect using Devicenet to Wago. I had some experience...
159
Sigh, DeviceNet noob... I have a 1756-L55, with a DeviceNet module, and 10 PF700 all commanded with DeviceNet. One of the PF700's blew up...
143
Good day Forum Members I got a older Lincoln welder and hoping to make it work at our shop. Welder in question is the Lincoln Power Wave 455M...
215