DH485 Network node questions
matthew1
Feb 2011
virginia
100
Hello all,
I have an Allen Bradley DH485 network that currently has three devices.
Micrologix 1500 LSP series C w/1764-24awa base node 1d (main)
Micrologix 1500 LSP series C w/1764-24awa base node 1d (CIP)
PV1000 2711-T10C3 node 3 (max allowed 6)
1761-net-aic
Network has always worked fine but very slow update.
I’m trying to install a Redlion Data station plus on the network.
Model DSPGT node 6 Plugged into DB9 port on Net-AIC.
When I install the data station on the network it comms and records data. It also gives me a 615 fault on the pv1000. The user manual states that this means there is a duplicate node on the network. In the Panel Builder program for the 1000 its only pointing to one node main_panel node 1. The touch screen controls functions in both of the PLC's.
In both comm setups in the 1500's the message instructions both point to node 2.
In Crimson 3 the DSPGT Its programmed to comm. with node 1 and be node 6. It generates initial token. Baud is the same as 485 networks.
So is it possible the network is setup wrong with existing duplicate nodes and working? If so should the node address be changed to 1d and 2d and change message set up?
Any help is appreciated.
Thank you in advance.
Matthew
If I am following your network setup correctly then yes. The ML1500's will have to have different node addresses if on the same network. In fact all nodes will have to have a unique address.
Hello Mickey thank you for the reply. Sorry mine has taken so long.
Thats what I thought. The PV1000 is limiting the nodes to 6.
RSLINX's 00
1500xxx 01
1500xxx 02
PV1000 03
x 04
x 05
DSPGT 06
Is RsLinks included in the 6 allowed node's limiting the actual decimal node adress to 5?
I have an allen Bradley system in which there is two micrologix 1200 and two panel view 300 and a Rsview 32 connected on DH485 network with the...
1,776
Hi, i am trying to create an DH485 netwrok which will consist of 2 ML1500 using ACi units for data acquisition back to a pc. i understand how...
2,009
Hello All, I am currently troubleshooting a communications issue regarding a DH485 network. The network contains PLC1, PLC2, and PLC3, all AB...
3,804
So I am attending a site next week that is reporting PLC communication issues between its three SLC 5/03s (PLC1, PLC2, PLC3). PLC2 communicates...
1,803
Hi, I want to know if and how i can bring up my DH485 network to a ethernet/ip. My network is setting with 1747-aic and 1761-net-aic. So i...
2,299