Direct logic PLC, DL-06 I/O expanssion
e_pramod
Feb 2005
29
hello,
I have used DL-06 PLC in One application,
I used 4 chaneel 3 analog input module b'se 8 channel AI module is not available in DL-06 series & One ethernet module. 24 digital output required in my application ,how expand the i/o does any expantion module is available in DL06 PLC?. B'se this PLC support 100 I/O, but how this expansion posible in DL-06 PLC
The maximum I/O count is based on a configuration using four discrete I/O expansion cards, which have more points per card than analog. It also doesn't allow for ethernet or other expansion units, which take up an I/O slot.
You have some choices. You can upgrade to a DL-205 PLC, which has more I/O slots. You could add another DL-06 PLC and use a serial communications link beween the two PLCs to get the I/O status into the base DL-06. This is how I'd go.
Terminator I/O would work using the MODBUS RTU Slave interface and DL06 Port 2 or the new D0-DCM communication card. You'll have to write the code but fortunately it's fairly easy. Even the T1H-CTRIO is usable in this mode.
Hey, I am entirely new to PLC's and am trying to help my friend with a project. He wants to take the signal from a PNP photoelectric sensor as...
2,241
Could you help me please? I want to communicate a Red Lion HMI (G307K200) with a PLC Direct Logic 06 (D0-06DR). The supplier of Red Lion...
3,293
I have worked with Automation Direct line of PLCs before but it has been several years. I am looking to back up (save) PLC programs for my...
2,416
I have a DL205, dl250-1 cpu and a ecom100 module. I have a 16bit register utlizing bits 0-10. I am trying to figure how to set up a sequence for...
1,242
Hello, I am working with a DL205 with a DL250-1 CPU and a H2-ECOM100 module. I have recieved a modbus map that I am working with. The program that...
1,379