Energy Monitoring System
As I [am] concerned [because] those clamps are current transformers. And [a] stupid question comes up: How many wires the same phase I can put in to [a] single clamp?
First, please confirm that you are talking about clamp-on current transformers. If so, then you can put as many wires as will fit into each current transformer. You do have to make a rough guess about the maximum load of all the wires, and make sure that the expected maximum current does not exceed the current capacity of the CT.
If you are measuring the load on each leg of a circuit breaker panel, usually you can put two current transformers on the main incoming L1 and L2 cables (not the neutral) to read the total load. This is much easier than trying to fit a big bundle of wires into a CT. To read the total load, you need CTs rated for the ampere rating of the main breaker.
Since the title of your post is "Energy Monitoring", I assume your final goal is determining electrical power. For that, one generally multiplies instantaneous currents and voltage drops. If so, you must account for phase lead or lag in the clamp-on current probes. I have seen up to 10 deg in some models. At low power factors any phase shifts greatly affect the calculated power.
Hi! My client has requested an energy monitoring system with a capability of entering production of each machine by the operator. The system must...
2,157
Did a forum search but did not see anything recent. What are people using to monitor energy usage at their facility? I am being tasked with...
31
6,793
Hi, i cant establish communication between fatek plc with an energy meter, both capable for modbus tcp, i did with modscan but fatek plc does not...
153
I want to calculate the energy consumed from instantaneous power. Can this be done using the TOT block with timebase set to Hour?
696
Hi All, We are planning Establish communication between Power Energy Meter (Schneider PM5320) with Rockwell PLC. I am unable to get the Assembly...
763