FX5U Label name incorrect

pacak

Member
Join Date
Sep 2006
Location
Arad
Posts
65
Hi there!

I'm new to GX Works3 so please bear with me.
So far I've created a new project with an FX5U PLC and tried to add some global labels with input devices.
At the third label (E-STOP_2_OK) when I press the Check button on the Global Label page, the background of the label becomes red.
If I recompile all, I get the following error message:
Label name is incorrect. 'E-STOP_2_OK' is reserved word. Please modify the label name.

Any ideas?

reserved word.JPG
 
Last edited:
OK. So it looks like GX Works 3 does not like dash in a label.

Attachment is from the GX Works3 Operating Manual, Appendix 2, reserved words, symbols which cannot be used.
I do not see any dash in that list.

Also looks like a label has to be a single word: bla bla not ok, bla_bla is. Could not find this mentioned in the above manual or the FX5 Programming manual (Program Design).

Mitsubushi, this does not begin well!

reserved word 2.JPG
 
Hi!
Thanks a lot!
I thought about it but could not find the issue date.
It is in the Revision section. Now I have a doc from April 2021: SH(NA)-081215ENG-AD
 

Similar Topics

Hello there is a way to do the polyfit on 3rd degree on this plc. for imput i have a munimum value of 5 X and 5 Y value for example Measured...
Replies
58
Views
2,633
Hi All, I am after some assistance setting up kepware to take tag data from an FX5U PLC, I have tried many many port numbers and still cant get a...
Replies
2
Views
164
Hi, I am trying to send data register type (D) from Toyopuc PC10g to FX5u. Does it possible to connect both plc using fx5u features which is...
Replies
1
Views
30,625
Hi, I have a Mitsubishi FX5U PLC where I cannot established communication via ethernet port of my computer. Search all videos and follow all the...
Replies
3
Views
1,235
Hello there! I try to to drive a HF-KN13 servo motor with a FX5U PLC through MR-JE-10C. I tested the connection between the servo amplifier and...
Replies
1
Views
681
Back
Top Bottom