Help going online with SLC 5/04

For the last pic's your SLC is set to DF-1, 19200 baud.


In RSLinx you have Device set to PLC-CH0 which is for PLC 5's


Change the Device dropdown to SLC-Micro, and set the baud to 19200, then do autoconfigure.



Also, you will need a null-modem cable or a standard cable with a null-modem adapter and a female to female gender changer.
 