I have an Analog I/O card with the input signal range of
0 to 5 V, 1 to 5 V, 0 to 10 V, –10 to 10 V
I want to use it with 24v battery, so if the battery goes lower than certain volts system indicate for charging.
how can i use this card with 24v, or how would i drop the voltage but keeping the watts same.
Thanks in advance for any help.
You could use a 7k and 5k resistor in series, and then place your input in parrelel with the 5k resistor. This will give you 41.7% of the total volts across the input and 10v when the battery is at 24v. However if the 5v resistor opened you could end up with full voltage at the input.
-Mur
-Mur
I did something like this with remote racks to monitor each 24vdc supply. All we wanted to know is if the 24vdc was there so any kind of voltage divider to keep it in the input range. Our inputs could take 30vdc but only measured 10vdc. In the MMI it would alarm and the screen would tell the operator which supply and rack the problem was. It worked quite well. Sometimes a prox would short and take out the supply so up pops a screen warning and that way they could tell the electricians where the problem was.
Actually I am doing my final year project. I am bulding an AGV(Automatic Guided Vechicle). I want to build the automatic charging docking station for that unit, so whenever the power goes down at certain level AGV would go on docking station for charging.
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
88
Hi all, i was trying to learn the analog card and got pulled off. now i am asking for your help again. this is what i have. all i/o are enabled...
1,307
Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
1,202
We have an omron CJ2M-CPU12 PLC that we are having issues with an AD04U analog card. it is connected to a K type thermocouple sensor. The card is...
602
Hi all, While i am not new to omron, i'm totally new to the analog part and lost. i have a CJ2M cpu 33. then there are 4 i/o cards card 5 is a...
26
2,583