Hi,
I have some remote IO connected to my S7-317-2 PN/DP system.
I have 1 particular profinet remote IO which is not important to the system, and so I want not to stop the CPU in the case this particular remote IO fieldbus or module in the fieldbus is inserted or removed.
I read there is OB83, but looks to be only for S7-400, I have already loaded OB82.
If I remove the hardware during run, the event is:
STOP caused by removing/inserting module (OB not loaded or not possible, or no FRB).
Is this possible so be able to insert/remove without causing stop?
Regards,
I have some remote IO connected to my S7-317-2 PN/DP system.
I have 1 particular profinet remote IO which is not important to the system, and so I want not to stop the CPU in the case this particular remote IO fieldbus or module in the fieldbus is inserted or removed.
I read there is OB83, but looks to be only for S7-400, I have already loaded OB82.
If I remove the hardware during run, the event is:
STOP caused by removing/inserting module (OB not loaded or not possible, or no FRB).
Is this possible so be able to insert/remove without causing stop?
Regards,