Insufficient resources exist on SOME_CLX_PLC to support Alarm & Event functionality.
Yashka
Nov 2019
WV
91
Hi All
AB question. Please help me sort out this error in FT View. I've attached the screenshot with available memory on this ControlLogix 1756-L61 V20.19 controller. I have the same PLC with similar occupied resources but one is working fine. Factory Talk Studio is version 10.0
What is going wrong?
Thanks in advance!
I've had a similar issue, I think the program works "fine" but I ended up going up a PLC size and put in L7x series.
Can you look at studio5000 task monitor and connect to the PLC? Unsure if this tool will give anymore info.
edit - if you have the support contract go to BF22147 unsure about the rockwell contract and me posting out of it.
From memory to recompile the actual memory, you'd have to flash the controller and then check code for errors and download to PLC.
Yes, I did it first of all. All working smooth and fine. CPU load < 30%, Network load < 5%, memory ~=50%. Any artifacts were found.
Unfortunately, I don't have.
Could you explain me a little bit in detail? Do I have to download my current program and restart PLC for free memory?
From your picture the largest free block of memory is only ~100k, so if you flash the firmware and redownload your current PLC program it may make your largest free block of memory larger.
Or upgrade your PLC to the next larger memory size.
OK. I've got it, thanks.
I am getting the following error on factory talk and cant find any explanation for it "insufficient resources exist on WTP_PLC to support alarm...
2,774
Dear Experts We are using 3 control logix systems (3 controllers for three different areas) on a cement plant. On two Ares tags are almost...
2,522
We have purchased Controllogix system for our white cement plant at Kohat. And we are facing problem in communication since we purchased it. Our...
2,694
S7/TIA v18: Status Message "Insufficient memory space on the memory card"...... Hi, Please can anyone help me with this? I've been trying to...
27
2,393
Hi, We had a power bump last night. After we got everything back up an running I had an alarm come in. Unable to subscribe to alarms from...
2,533