I am trying to connect kepware OPC server to S7300 PLC. The task is to read Data block DB40 into OPC. As it is my first experiance with Kepware to S7300 i am facing problem with Tag addresses. Data block's structure shown in the picture. any one help me to configure tag addresses of kepware for this data block.
Thanks,
Khalid Rafique
In Kepware, First define the Channel of the correct type e.g. "Siemens S7 Ethernet" then the device: S7300. Add tags to the DB as DBXXX.DBWYY
Nick
A few years ago, I created an archive of Kepserver to read a S7300 with RSView32. When you configure the driver, channel, etc and get to the tag database, you have to create a tag with a nemonic name (ex Motor1_RPM) and asign the DB block with point and another db addres depending if you want to address boolean, a float, a DWord, etc. I don't remeber how to do it exactly, because i desinstalled Simatic S7, but in my kepware file I have tags like:
Addr: DB31.DBW28
Type: Word
Addr: B100.DBD154
Type: DWord
DB31.DBD102
Type: Float
As I told you, I don't remember how you asign the value to the right side of the dot DB40.????, but you hav to follow the rule to make a float, word or whatelse.
The addressing is like the following table(taked from Kepware Help)
Data Block
DB1 - N.DBX00000.b - DBX65535.b
1-N is DB Block Number
.b is Bit Number 0 -7
Boolean
Read - Write
Data Block
DB1 - N.DBB00000 - DBB65535
1 - N is DB Block Number
Byte, Char
Read - Write
Data Block
DB1 - N.DBW00000 - DBW65535
Word, Short, BCD
Read - Write
Data Block
DB1 - N.DBD00000 - DBD65535
Dword, Long, Float
Read - Write
Hope it can help you. If you can show a JPG of the Siemens database of DB40, I will try to remember to make a more useful post.
If you're using RSview32 and kepware4 you don't actually need to define tags in kepware at all. In Rsview32 define the node and then when making a new tag: select the OPC node and enter the address as ChannelName.DeviceName.DBXXX.DBWYYY.
Nick
Thanks all of you. actuelly i was busy at some other project. Now i have tested but the problem is still there. i am receiving "bad" quality in kepware. the connection to the PLC is usb MPI cable. the cable is OK i can access PLC through Step7. I have attached pic of S7 project. what is required is to read elements of DB40,41,42,43. I use DB40.DBW0,DB40.DBW2 ...
Thanks,
Khalid Rafique
Dear Khalid,
Kepware doesn't work with the USB MPI cable, you need a RS232 MPI cable.
You can visit the FAQ section of kepware and they have an alternate NETLINK cable which u can use.
I have a strange Kepware issue I have been dealing with for a few weeks. I have Kepware setup with the Omron NJ Ethernet driver and reading in...
98
Hi All, I am after some assistance setting up kepware to take tag data from an FX5U PLC, I have tried many many port numbers and still cant get a...
164
Im trying to get data from AB guardlogix controller using Kepware in a remote location but it seems that version 6 can only support contrologix...
443
Hi, Have anyone came across issue with Kepware or Linkmaster not returning correct values (Unknown Quality) for some tags From OPC DA Client...
677
I’m attempting to configure KEPWare to poll a Modbus device via Modbus TCP/IP. However, everything I’ve tried results in an error being reported...
415