I have a compactlogix L35E and my analog input signals are bouncing all over. It's a 1769-IF8 card. We measured the signal at the wire going into the card with a fluke clamp on meter and the 4-20 mA signal is steady as can be. We have changed the card and the same issue exists.
Any ideas would be much appreciated.
Thanks!
Austin,
Try sourcing a 4-20 mA signal with test source. Your Fluke may be able to source. The raw values should smooth. Also try with all card inputs removed, this should validate your card and noise free PLC power.
Electrical noise is a big problem with analog inputs, check wire shielding is grounded only at one end (the PLC panel end).
Any new VFDs nearby? These are the biggest noise generators.
May need to install 4-20 mA signal isolators. I have fixed several noisy input problems by installing these. They regenerate the 4-20 mA from local power.
Good luck
Paul
Thanks for the feedback. We had a 24V relay where a 120V was needed,somehow that compressor was still starting!
Scott
Hello, We have had a machine running for the last 10 years. It has 2 x Kinetix 300 drives. Around a year ago, one of the drives failed. We were...
432
Hi All Trying to get the PLC to send a commant to the printer to prinnt a lable. evarything is setup except RS linnx cannot see the printers and...
388
Hi All I'm trying to connect two zebra printers to th PLC through Ethernet. I can ping the Printer through my laptop connected to the private...
366
Hi, I recently tried to change the IP address of my 1769-L35E Series A, since doing this the MS indicator is flashing red and the NS indicator is...
936
I have a problem and I can't find anything about it in the Rockwell Knowledge Base. The problem is that I am losing communication with a...
1,244