The case is having the plc in a place that is 10Km distance from the pressure transmitter which is the PV to the PID ,so the response take a ong time,when we increse the speed of the pump by giving SP the response take time and it became more than the SP.
how to slove this?
Hello maher731;
You are adding a delay to your process through the time-gap of the response time on your transmitter.
Can you reduce the delay, say change the transmission parameters of the signal from the pressure transmitter? Think of dedicated-line modem, RF transmission (look at Siemens WiPS system, for example:
http://www.sea.siemens.com/instrbu/docs/pdf/wireless_solution_cutsheet.pdf)...
If you plan to try to compensate for this delay in your program, you can always try Feedforward control, or making the derivative parameter of the PID controller large enough to anticipate the changes in PV. But that sould be done by an experienced engineer.
Hope this helps,
Daniel Chartier
Hello PLCS.NET! I was wondering if there are options in the market which have distance to tag well as ID of the tag? They need to work in about a...
1,749
I know some folks here deal with long distance fiber so I thought someone can sanity-check this one for me. Here's the background. Our IT has...
2,149
Hello, We need to communicate Mitsubishi vfd (E700 Series) of around 32no's over a long distance around 2000meter from Mitsubishi PLC control...
2,946
I have RSLogix 500 standard, And RSLogix 5000 Mini. I want to be able to work with Micrologix and CompactLogix PLCs. Both of the software packages...
2,504
Hello. I have very little experience with PLCs so please bear with me. Problem: We have a pipe with two meter systems that are 10 miles apart...
20
3,175