Modbus to Ethernet
Dale87
Feb 2022
Illinois
61
What's the cheapest way to go from modbus rtu rs485 to Ethernet IP or TCP. I've got some power transducers I'd like to read some modbus addresses, they're only rs485. I've only got fiber located where they're installed so to get it back to either the HMI or PLC id have to go IP or TCP. A lot of places make a converter but most are $1,000+ dollars. The power transducers are only $300.
Same answer as I always give, S7-1211. Although it doesn't have RTU onboard, so you'd need either a communications module or a communication board for RS 485, which would probably push it over the price of the above post from Ken Roach. May be worth it if there's a chance you need the additional functions in that location.
Moxa Nport models (if you can read Serial over TCP modbus protocol)
Moxa Mgate (Modbus TCP)
Teltonika TRB245 or TRB255 (Modbus TCP)
Especially if you already have an enclosure with space, cheap but not the absolute cheapest: Micro 820 or Click. That also gives you a bit of I/O that might be useful. I would probably use Click C0-11DD2E-D ($212, or relay outputs for $4 more) for that unless I had a reason to use an analog model ($253-$269) for some additional monitoring in the area. The 820 would cost a bit more and depending on the application, maybe should also use an isolated serial module instead of the on-board port. Add a power supply as needed for a bit more cost.
I would definitely use the Click Plus.
Software is free, it supports runtime updates (~online editing).
They're reliable and well supported.
You can write logic to manipulate the data as needed for your application.
I would not use a Micro8x0. I had my first experience working with one of those this week where all I needed to do was add a single new remote node to a gateway system for radio telemetry done by others. The programming looked straightforward, but making the changes was quite a PITA. First I had to download and install the latest version 13.0 of CCW which took an hour.
Then I had to study how the data types for the MSG_MODBUS work and it is a little weird. Then I had to study what the differences are between Logical Values, Physical Values, and Project Values so that I could determine how and if I needed to edit the numbers associated with the instructions I copied and edited.
Then I had to add entries to the Ethernet Modbus Map for the TCP side and sort out the data types for each.
I could not do any of this live because I am not paying for the developer version, so I googled how long the PLC might be stopped for a download and was shocked. It was not a problem for this job and took less than 2 minutes since the program is so tiny, but that is still absurd.
Not a fan.
Not a fan.
I use them "micro 8××" on the "slave" end of telemetry projects where I just need a few IO. Absolutely awful, I shake my head every single time, and ask myself why I did it......
I do not understand the question.
What is Ethernet IP ?
Do you mean Rockwell's EtherNet /IP protocol?
What does TCP mean? TCP is a transport layer protocol and will not be helpful by itself.
We know that the power meters use Modbus RTU over RS-485, which you clearly specified. But what is the protocol you are converting to/from?
Does anyone have any recommendations for Electronic Circuit Breakers with 0V Terminals built-in and Fieldbus (IO-LINK, MODBUS TCP, EtherNet/IP?)...
195
Hello, Sorry, my knowledge of communication protocol is limited, so thank you in advance for your answer. My question; I want to get 5 values...
867
Hi All, Trying to help a client who has a project that was started with Schneider STB remote I/O, but they are still waiting on the STBNIP2212...
1,915
Hello all, I was wondering if you clever people could help me, please. In the past I have used a standalone L33ER CompactLogix PLC with the...
1,527
We need to hook up the existing Honeywell AHU controllers to the new SCADA system. These Honeywell controllers (XL50 series) uses Lonworks as...
1,742