Multiple Panelview 5/04 DH+ problems
Zackbo
May 2015
Charlotte
So I've connected 3 existing 5/04's over DH+. Each PLC has a local Panelview with DF1 to the RS232 port. After a few hours, one Panelview will start communicating and writing to registers in one of the other PLC's!! Anyone ever seen something like this? How do I make it stop? I have DF1/DH+ passthru disabled on all 3 5/04's.
To be clear your Panelviews are connected to the PLC's serial port?
Check for messages instructions using the DH+ network that reads or writes between PLC's. Or the SLC's are using "Global Status Words" to communicate across the DH+ network.
I agree that MSG instructions are more likely to be the root cause of the problem. Code doesn't just change after a few hours.
Check to be sure there is no logic modifying the DH+/DF1 passthrough enable bits.
Check the PanelView terminal programs to see what the DF1 destination node numbers are. Really, they should all be Node 1 talking to Node 0, because DF1 point to point ignores destination node numbers.
I don't see a way for an SLC-5/04 to turn on passthrough and invent a target address that's not in the packet.
But then, this morning a man came out of the woods next to my house carrying a ukulele case and wearing a rubber ape mask. So nothing really surprises me anymore.
Hi Guy's, I have a project to link multiple HMI's to multiple PLC's that will all run the same process. I want to be able to call the mimic from...
1,585
Can anyone tell me if it is possible to use Factory Talkview ME programming software with a new Panelview Plus HMI to read tags from multiple SLC...
1,642
I have what I hope is a simple question. Can I run two PanelView Plus touchscreens with identical applications talking to the same compactlogix...
19
8,015
Hello everyone, I have to program a PanelView plus connected to a Compact Guardlogix controller. The client has specified that there should be an...
3,168
I've never tried to do this before, and I've thought of a few possible solutions, but they all feel like kludges. I have a control system...
6,891