I dont understand what the reserved S7 Basic connectiosn are for. Remove the reservations !
I forgot to ask what is connected to the Profibus network called PROFIBUS(2) ? It seems to be empty.
Apart from that, 3-4 panels plus at least one configured connection may be too much for the slow MPI backplane over which all the comms must pass.
I am beginning to think this is the problem. Since you have intermittent problems already with only 3 panels, it does not seem to have to do with connection resources (the problem wouldnt be intermittent in that case).
If I were in your shoes I would start considering replacing the 316-2DP for a 315-2PN/DP or a 317-2PN/DP (the 315 will probably be performant enough). Then connect all HMIs to the PN port, connect all IO to the DP port (no panels on the DP port !), and keep the CP343-1 for the ISO-on-TCP comms to the other PLC.
I forgot to ask what is connected to the Profibus network called PROFIBUS(2) ? It seems to be empty.
Apart from that, 3-4 panels plus at least one configured connection may be too much for the slow MPI backplane over which all the comms must pass.
I am beginning to think this is the problem. Since you have intermittent problems already with only 3 panels, it does not seem to have to do with connection resources (the problem wouldnt be intermittent in that case).
If I were in your shoes I would start considering replacing the 316-2DP for a 315-2PN/DP or a 317-2PN/DP (the 315 will probably be performant enough). Then connect all HMIs to the PN port, connect all IO to the DP port (no panels on the DP port !), and keep the CP343-1 for the ISO-on-TCP comms to the other PLC.
Then why is one port setup as and connected to MPI in the NetPro screenshot ?Are there MPI partners connected to the MPI port on the 316-2DP ?
- No, both ports are configured as DP.