I dont understand what the reserved S7 Basic connectiosn are for. Remove the reservations !
I forgot to ask what is connected to the Profibus network called PROFIBUS(2) ? It seems to be empty.
Apart from that, 3-4 panels plus at least one configured connection may be too much for the slow MPI backplane over which all the comms must pass.
I am beginning to think this is the problem. Since you have intermittent problems already with only 3 panels, it does not seem to have to do with connection resources (the problem wouldnt be intermittent in that case).
If I were in your shoes I would start considering replacing the 316-2DP for a 315-2PN/DP or a 317-2PN/DP (the 315 will probably be performant enough). Then connect all HMIs to the PN port, connect all IO to the DP port (no panels on the DP port !), and keep the CP343-1 for the ISO-on-TCP comms to the other PLC.
Are there MPI partners connected to the MPI port on the 316-2DP ?
- No, both ports are configured as DP.
Then why is one port setup as and connected to MPI in the NetPro screenshot ?
Hi Jesper, thanks again for your time.
- I tried that before, I increased OP to 7 and decreased S7 Basic to 4. I didn't make any difference.
- I believe it is used to talk to the other remote PLC. Talks to one PLC via ethernet, other via profibus.
I am beginning to think this is the problem. Since you have intermittent problems already with only 3 panels, it does not seem to have to do with connection resources.
- Yes, those are the two we are considering.
Then why is one port setup as and connected to MPI in the NetPro screenshot ?[/QUOTE]
- Thank you for noticing this! All the other PLCs in the plant use both as DP, I didn't notice that it was different in this case. This means I can replace it with a CPU 315-2 DP which is half the price of the 317.
First post....thanks for all the help in the past.Primarily an AB guy but we have a new process with a Siemens s7-200 in it.In random bursts the...
2,039
I have an Allen Bradley temperature switch that I am trying to use in studio 5000. I am getting the message "Unable to interpret the IODD file"...
111
So I had an odd request from a customer for the above. I have written the logic and tested it all in one PLC with only using 7 outputs and 7...
487
I have been requested to test this proportioning valve for PLC control of flow/pressure. Dwyer Series SVP Proportioning Solenoid Valve The flow...
449
Howdy guys - Looking for some insight on the MAM instruction. Had an interesting one today: I performed a controller upgrade on an older system...
459