Omron PLC IO Bus Error F
Jothiswarup
Apr 2014
Somewhere
33
Hello all,
Recently I am having fatal "IO Bus Error F" on a system. This happens once or two a day randomly on a system which has been running for more than 10 years.
There is green run light and red "ERH" on analog module is and all other modules/PLC are off when this happens.
I replaced PSU, PLC (CJ2M) and Analog module (AB081-V1)
I/O table matches and verfied
Everything goes back to normal on re-boot.
PLC goes into error again intermittely. Any thoughts?
I've had the same error show up on a CJ2M with a MAD42 module that we traced back to poor grounding on the PLC power supply in one instance and damaged cabling on one of the outputs in another. The damaged cable was easy to diagnose, it was a hard fault. The poor grounding was trickier to find.
There are analog modules in slot 0 and 1 after CPU. It was module on slot 0 failing and I swapped both modules and it started doing on slot 1. Same result after replacing with new analog module.
I will start with checking ground connection. It is trickier because it happens very randomly.
Hi all, I have error on my PLC that say on 7-segma HH and this issue come two to three times and I had checked the PLC which is tight and they...
619
Hello Guys, I have a packaging machine in the company that I work for that have 8 Omron VFDs (3G3MV ) that are controlled via Modbus with CJ1M...
642
hello i wanto asking the setting and program for communication modbus The plc that i use is CJ2m cpu31 i use extra communication module...
1,703
Hi everyone, Its been my first time to handle a power monitoring project where i will be using Omron CJ2M cpu 31 with a SCU41-v1 for its...
7,307
What is the difference between ths CS1W-PRM21 and C200H-PRM21? I am trying to setup my hardware in the PLC program but only see the CS1W-PRM21...
2,046