Incredulous, an it seeks by "overload" only finds about Motor, somewhat that does not relate to PLC!

Need of practical references about the utilization of PLC with transistor output.
It specified direct current 100mA and peak 300mA
Output direct connect Contactor overload is 20%. Therefore, some
project utilized outputs with overload? Had stability and time of life?

Operation down the 30ºC of operational limit, trink is acceptable. But not have table to check.
 
I would avoid going over 75 mA or so steady state load on these outputs. I would not go over 100 mA, since that would definitely shorten output life. The 300 mA figure is probably a momentary load, to accommodate inrush on relay coils or such. You might "get by" using this output on a solenoid with a 300 mA max inrush current, but only if the duty cycle was low.
 

Similar Topics

I'm looking for how others do it. I need to start a 1 phase motor. I have always used a regular 3 phase Motor Protected Circuit Breaker and looped...
Replies
9
Views
175
My R55 Ingersollrand is tripping on motor overload and im falling to see the trip history it is writing Acquarring texts
Replies
0
Views
137
Hi, Again, a topic about Kinetix 5100 servo drives. The controller is L33ER. The servo drive are 2198-E1020-ERS with a TLP-115-200-DJMC2A. There...
Replies
0
Views
559
Hi, I'm using E300 as E3 Plus in emulation mode. E300 is Rockwell Automation's overload relay. But I get hardware fault when I enable Ground...
Replies
0
Views
478
Sometimes I see that a thermal overload relay (combined with a protection against short circuits) is used instead of a MPCB (motor protection...
Replies
2
Views
927
Back
Top Bottom