Panelview DH+ to RS-232?
Old No. 7
Jun 2010
Ohio
173
I have a DH+ Panelview Standard that I need to connect to a SLC 5/05. Is there a way to convert from the RS-232 port on the SLC to DH+ (or Ethernet to DH+)?
I really don't want to have to replace all the Panelviews.
Do you already have SLC 5/05 talking to the panelviews?
I all your looking for is connectivity to the 5/04 processors, install a controllogix bridge. What this would consist of is a controllogix power supply, 4 slot rack, 1756-ENBT(ethernet card), and a 1756-DHRIO(DH+ card).
You can then get to all your processors on the DH+ network. With proper configuration, you can even message to the different processors thru the bridge. You cannot however download/upload to the panelviews. PanelBuilder 32 does not allow it.
This would be a less expensive solution than changing out all the processors.
This is on five different pieces of equipment. All had Panelview Standards and SLC 5/04. We are updating the processors to 5/05's and adding a remote Panelview Plus. I thought (incorrectly) that we could communicate RS-232 from the 5/05 to the Panelview Standard, so now I'm hoping there is a converter to do this.
Anyone have experience with the DataLink DL3500?
http://www.protocolconverter.com/products/dl3500dh+df1.htm
For connecting to a Micrologix through a 1761-NET-AIC, the manual specifies that you should use "RS 232 Communication Cables Cable, Cat. No...
1,373
Was wondering if anyone had any suggestions: I'm trying to connect to an old PanelView 1000 Touchscreen model# 2711-T10C16L1 via RS-232. I'm...
3,695
Hi again, I have many times used RSLinx to connect to PLC's with the DF-1 serial driver and a USB-RS232 adaptor. No problems. Now I'm trying to...
4,379
Hey guys, I have a quick question about connecting a PanelView Plus to a Micro850 using the RS-232 port on both devices. Originally I had the...
3,686
I need to communicate with a panelview plus terminal to upgrade the firmware. My question is, can I use a regular RS232 serial cable to...
2,789