PanelView Plus 600 Ethernet'ed to a MicroLogix 1400 Not Communicating

sopenco

Member
Join Date
May 2008
Location
Cochabamba
Posts
49
Could someone please help me figure out what's missing here?

I have an ML1400 and a PV+600 both connected to an ethernet switch. If I connect the switch to my network and set the ML1400 to DHCP, they talk back and forth just fine. I can't get them to talk in any mode without the switch being connected to the network.

Thanks in advance for any help / suggestions!
 
I would venture a guess that when the switch is not connected to the network both devices' DHCP protocol will time out resulting in a 169.x.x.x IP on each. Perhaps they are not defaulting to any IP at all if one is not assigned. When you are not connected to the network, can you access either one through the switch?

Some suggestions:
1. Assign DHCP reservations for those devices MAC's so that they always get the same IP while connected.
2. Assign static IP's to each device and exclude those from the DHCP server so that if/when you do connect to the network you won't get conflicts.
3. Leave them connected to the network.

" I can't get them to talk in any mode without the switch being connected to the network." <--- any mode being something other than ethernet?

Good luck
 
If I’m not mistaken, neither device has “auto detect” with regards to cable connection where the switch probably does (most switches do). Do you get a “link” status when the two are connected to each other without the switch?
 

Similar Topics

Hi I have a number of the older PanelView Plus 600 HMI's (2711P-T6C20D, Ser D) that I want to update to the latest firmware. I believe that the...
Replies
10
Views
475
Hello , I have an HMI of PV+ 600 (2711-T6M5D) Ser A Rev B, This HMI doesn't have the ethernet port i have to take backup through communicate...
Replies
5
Views
662
Hello all, I copied the MER file from one PanelView Plus 600 to another one, using a USB drive. On the new HMI, I copied the MER file to the...
Replies
4
Views
634
Hi all, I have an old PanelView Plus 600 (2711PC-T6C20D8) that I am repurposing on our site - I have flashed the firmware to ME version...
Replies
4
Views
987
Hello Team, I have a question, I have been working with a panelview plus 600. But I have deleted all the .mer directly from the HMI, after that I...
Replies
16
Views
1,711
Back
Top Bottom