Thank you all for your input and suggestions!! Ended up replacing the power supply and 6 or 7 meters started pulsing almost immediately. Seems like the rest may be configuration or wiring issues with the individual meters. Should hopefully be able to get most figured out here soon. Thanks again for everything!
 
Is your DI card rated for the speed at which you are trying to see pulses? Often a flow meter will require a high speed input card.

I've been installing a ton of those lately. You can usually circumvent that by programming the flowmeter so that the pulse is more gallons per pulse. It would have to be very fast flow with an undersized flowmeter to need something like an allen bradley high speed counter.

Some plcs the pulse is too long and you need to use a one shot function so that the pulse only kicks once per count. Also my experience has been that the di card will read too many pulses unless the pulse length itself is too short for some older processes to catch on a scan. I'm talking mostly about magmeters and coriolis though to be clear.

Lots of potential problems with integrating flow meters.
 

Similar Topics

Dear all, I don't know why setup of password became challenging and weird. After setting up the password and try to upload the ladder from the plc...
Replies
3
Views
178
Hello! New to the forum and new to PLCs in general. We have an ABB AC500 PLC (circa 2012?) and we are using CoDeSys (version 2.something). We're...
Replies
0
Views
646
I am operating a Siemens IM151-8 F Processor with 4 6ES7-134-4NB01-0AB0 2 channel thermocouple cards. I am getting no reading from any of the...
Replies
31
Views
6,107
I am working on a Micro 820 with a 2080-MOT-HSC high speed counter module. I am trying to read the pulses from a Signet 515 paddle wheel flow...
Replies
0
Views
718
Hi everyone, I have an issue, how is it possible to read data from an XML file with Delta PLC? In fact, I have another device (ElectroCell from...
Replies
1
Views
1,148
Back
Top Bottom