Powerflex 750 series drive error message
Prayder
Jun 2014
Arkansas
254
I keep getting a Net IO error message F037 on a brand new drive and after researching it, AB says that it has to be connected to a managed switch. Why would that device have to be connected to a managed switch vs an unmanaged switch? Anyone know?
It's generally recommended to use managed switches in high-demand industrial networking applications because of the diagnostic features and the management features they provide.
In *some* applications it's a requirement, or more important than in others, because of features like QoS or IEEE 1588. Some of those applications (like CIP Motion or CIP Safety) can involve PowerFlex 750 series AC drives.
Fault Code 037 should be displayed in conjunction with a DPI Port Number. The host main board itself is Port 00 so it will just display "037" for a Net IO Timeout fault on the embedded EtherNet/IP port of a PowerFlex 755.
If this fault is immediate and persistent, then you've got some kind of network or PLC configuration error. The most common one is when you take the PLC offline for a download and the I/O connection breaks ! You can configure the drive to ignore those or display a warning only, but the conservative default is to trigger a Fault.
If the fault is intermittent, then you've got a noise or cable problem, which may be where the "use a managed switch" advice is coming from.
I was getting a Net IO timeout error message but now it is Network idle message. I didnt have all my remote modules configured for unicast connection over EtherNet/IP
Looking over the technical data for a PowerFlex 755 & noticed they specify a minimum enclosure volume for their drives: (1)When using a circuit...
549
Hi, I need some help on how to reset fault on the Powerflex 750 via ladder logic. I have looked through the parameter documentation and I...
9,611
Hi everyone, I have this issue with a PowerFlex 755 that it mount a Safe Speed Monitor option module. Frequently, while running, appear the error...
2,340
Hi, I am just starting with the drives and I have a Powerflex 750 drive which is missing the rating plug board from the inverter board. I check...
666
Is anyone else having looooong connecting times when using CCW to a 750 via a 1203-USB? It is taking upto 10 minutes to connect to drive or...
1,788